fec_uncor_detected

Hi

 

On a SN8600B i see a lot of errors of the type fec_uncor_detected

There are no CRC errors, nor any other physically layers errors logged

 

          frames      enc    crc    crc    too    too    bad    enc   disc   link   loss   loss   frjt   fbsy  c3timeout    pcs    uncor

       tx     rx      in    err    g_eof  shrt   long   eof     out   c3    fail    sync   sig                  tx    rx     err    err

306:  267.4k 156.0k   0      0      0      0      0      0      0      1      2.4k   1.2k   0      0      0      0      0      0     44.8k

 

 

fec_cor_detected     17790               Count of blocks that were corrected by FEC

fec_uncor_detected   44860               Count of blocks that were left uncorrected by FEC

 

 

What could be the cause of the increase of this error ?

Broadcom Moderator
Posts: 455
Registered: ‎03-29-2011

Re: fec_uncor_detected

hi Thomas,

 

can you check the bad_os counter in the portstasshow for the same port?  You do not have any PCS errors, so it leave the bad_os. Further, this link is not stable or good - you have 2400 link failure and 1200 synchronization loss.  Physical layers, cable or SFPs.




If this provided you with a solution to this issue, please mark it with the button at the bottom "Accept as solution".


Any and all information provided by me is not reviewed, approved or endorsed by Brocade and is provided solely as a convenience for Brocade customers. All systems and all networks are different and unique. If you have a service affecting network problem, please open a TAC service request for service through Brocade, or through your OEM equipment provider. If this provided you with a solution to this issue, please mark it with the button at the bottom "Accept as solution"