Network Advisor shows two switches in DOWN state - yet they're up

A couple weeks ago we had a power down at our data center.  When power was restored and we brought the SAN infrastructure up we experienced zero issues.  However, when I looked at our SAN Directors via Network Advisor they both have a Red diamond for the switches as though there's a problem.  I also ran a Healthcheck against both switches and the healthcheck shows them as having a status of DOWN.

Anybody know what's going on or what I can do to get rid of the red diamonds?

Thanks.l

Frequent Contributor
Posts: 90
Registered: ‎12-26-2010

Re: Network Advisor shows two switches in DOWN state - yet they're up

try the `psshow` and see what it reports.

Contributor
Posts: 45
Registered: ‎02-16-2013

Re: Network Advisor shows two switches in DOWN state - yet they're up

psshow shows the following for both switches...............

Power Supply #1 is OK

V10H30,   AGC2M30HEG2      ,23-0000067-01, B,DELTA,ECD14020006     ,06,AGC2M30H

Power Supply #2 is absent

Power Supply #3 is faulty

0HEGC      ,23-0000067-01, B,DELTA,ECD14020006     ,06,AGC2M30HE

Power Supply #4 is absent

Frequent Contributor
Posts: 90
Registered: ‎12-26-2010

Re: Network Advisor shows two switches in DOWN state - yet they're up

as per this PS3 faulty; possibly its still not getting the power, or u need to confirm if its indeed faulty.

Contributor
Posts: 45
Registered: ‎02-16-2013

Re: Network Advisor shows two switches in DOWN state - yet they're up

Thanks SKT.

All is well now.  Apparently during the power outage the power supply to the directors was changed and the circuits were not activated which caused PS3 to be down/faulty.

Thanks a lot for your quick reply and assistance.